Hi Folks

I have some questions regarding M8 and M10 lugs and I'd be grateful for some help.

My 12V DIY solar system consists of 5 SCCs (200A total max), 2 Battery Chargers (120A total max), 2 LifePo4 batteries, a BMV-712 shunt, 2 x Victron 250A 6 post Bus Bars (+ve and -ve), and a Giandel W inverter. All in parallel via the bus bars (with the exception of the batteries, which are joined in parallel directly together).

1) My equipment, annoyingly, has different sized terminal posts/holes from each other. In principal, is it safe to use an M10 lug on an M8 stud/hole (using 8mm nuts/screws), as long as the surface area around the M10 lug is in contact with the metal plate surrounding the post/hole?

2) Is it safe and accepted practice to have multiple lugs on a single post/hole?

3) As mentioned above, I use Victron 250Amp busbars. Whilst 250Amps is enough for the total current from my SCCs and battery chargers (which are never on at the same time at max current), the current from the batteries to the inverter could be as high as 500Amps. Am I still ok to use these undersized busbars as long as my inverter lugs and battery lugs are on the same post (thus, in theory, no current from the battery is going through the bus bar) ?

4) If safe, what is the best way to mount 2 eg. M10 lugs together on the same post/hole? I can never seem to get 100% coverage of the upper lug on the bottom one.

This is what I have (ignore cable colours!):

5) Does anyone use a Littlefuse Mega with M10 lugs? If so, is this safe?

6) What is the tradeoff of doing 1-3 above vs just reordering cables with correct lugs as well as the Victron 600A busbars (apart from cost, of course). I'd rather not have to do this as long as 1-3 is safe, but your help would be appreciated.

Thanks folks!

Cheers

JT
In principal, is it safe to use an M10 lug on an M8 stud/hole (using 8mm nuts/screws), as long as the surface area around the M10 lug is in contact with the metal plate surrounding the post/hole?
I have done it. But literally “in principle” it is not ok on one hand and suboptimal on the other. It’s going to be held on tight enough, but on a W! 12V system there’s a lot of current potential that needs to happen at the point of contact.
Is it safe and accepted practice to have multiple lugs on a single post/hole?
No. People do it; I might do it if the battery to inverter was on the bottom and a small/thin meter/sensor ring terminal was on top or maybe an SCC output was on top in a smaller system. Most often, however, the bolt length will lose a couple of threads which weakens the potential holding power of the threads. I use a busbar.
Am I still ok to use these undersized busbars as long as my inverter lugs and battery lugs are on the same post (thus, in theory, no current from the battery is going through the bus bar) ?
I have done that when my system was 200W but undersized anything is a poor idea. Just get bigger busbars? Victron is quality stuff and will probably “take it” but fires don’t care about “probably.”
What is the tradeoff of doing 1-3 above vs just reordering cables with correct lugs
just buy the tinned terminal ends of the right size and an appropriate hex crimper for your probably 4/0 or 3/0 cables. That will likely cost nearly the same as new cables.
You are looking at what? 350A+ on that inverter? There is no trade off for safety.
I might consider W at 12V for myself but realistically? W+ is about the ceiling of practicality and safety in a 12V system imho 1. If you find yourself using larger cable lug hole sizes compared to bolt it likely will not be a problem. I am sure everyone ends up having that happen at some point. Just make sure everything is good and tight and check for heat under heavy loading.
2. Multiple lugs require that you do not place anything between them such as a washer. Again keep a eye out for hot spots.
3. I have no opinion.
4. See #2
5. Never tried it.
6. Temco makes a good assortment of lugs and cables. Not a bad idea to upgrade your stuff after you figure out what you need.

I endorse everything 12VInstalls stated in his post with one exception. If your system is going to be in indoors, and not subject to a harsh environment go with plain copper and not tin coated lugs. Copper to copper will be the best conductivity.

My 2 cents.
however this isn't financially viable
I have bought decent multi-sizes bare-crimp ring terminals that are decent quality and thickness for like $20
These assortments have enough pieces to do 4+ cables (one pair) and cost so little compared to small bags of a coupla sizes.
WindyNation sells 2/0 etc welding cable with crimp ring terminals and heat shrink for a decent price as well.
I wouldn't bat an eye putting a M10 on a M8 post.
Not being argumentative here, but for just a few bucks you can buy the right sized ring terminal ends; he’s doing W nominal and on 12V that’s ~330A+ - I’m admittedly ‘heat sensitive’ and oversize batt-inverter cables so I’m askeered of the reduction in contact area. ? Call me chicken.
permitted you put the highest current lugs the closest to the bus bars. Victron's 250A and 600A bus bars are drastically underrated and I would never bat an eye pushing way more than 250A through their 250A bars
the bus bar will accept that with plenty of threads; the three batteries I’ve experienced barely have enough bolt length in aluminum or brass for one ring terminal imho. Maybe I’m wrong or too skeered; could be.
I still think it optimal to only stack, say, the inverter feed over a battery cable that is in direct contact with the busbar though I do trust ABYC.
If your system is going to be in indoors, and not subject to a harsh environment go with plain copper and not tin coated lugs. Copper to copper will be the best conductivity.
True. Myopia of me living in Vermont makes me like the tinned terminals.
just would like to understand lug connectivity better
The more contact surface area the less the resistance. Less resistance less chances of heat build. Heat and fire is my OCD with stuff.
At 40- or 50A 12VDC nominal and higher I start getting nervous haha. So I go as far as I can to get stuff over done or perfect.
I endorse everything 12VInstalls stated in his post with one exception
And I endorse what you said?
Multiple lugs require that you do not place anything between them such as a washer
i should have said that; washer under the nut only.
Not being argumentative here, but for just a few bucks you can buy the right sized ring terminal ends; he’s doing W nominal and on 12V that’s ~330A+ - I’m admittedly ‘heat sensitive’ and oversize batt-inverter cables so I’m askeered of the reduction in contact area. ? Call me chicken.
I don't mean to argue either. Just in my opinion, 1/32nd of an inch all the way around seems like we are literally splitting hairs here.

barely have enough bolt length in aluminum or brass for one ring terminal imho
I am referring specifically to the bus bar in this case with a stud connection that has plenty of threads. A battery that has a bolt and barely enough threads to reach the proper torque is a different circumstance entirely. Hi All

Thanks for all of your feedback. The thing I didn't mention initially was that I am upgrading my inverter and battery cables (to 95mm2) so I am in the position to order cables with the correct lugs.

The not financially viable comment referred to upgrading the voltage of the system.

I have decided to go for a compromise solution regarding the lug sizing: the lugs connecting to the batteries, inverter, BMV shunt and the megafuses will be the correct size. The only m10-on-m8 will be the ends of the battery and inverter cables on the busbar. This will allow me to upgrade to a higher amp M10 busbar in the future if necessary. Does this sound reasonable?

I'd be grateful for any comments on my battery+inverter cables picture - is this the "best" way to mount 2 m10s on top of each other?

On the other studs of the busbar with cables coming from the SCCs (not pictured), I have no more than 3 m8's on each stud.

Thanks!

JT
only m10-on-m8 will be the ends of the battery and inverter cables on the busbar
Because a busbar is typically a plate there is no compromise of contact area. I would be ok with that- I think two of my busbar rings from the batteries are ‘too big’ and I used them because I don’t have another application for the larger ring terminals so I was being acceptably ‘cheap’ because I reasoned it was of no consequence.
comments on my battery+inverter cables picture - is this the "best" way to mount 2 m10s on top of each other
Well the nut threads are fully engaged so that’s a non-issue. And as long as the battery ring terminal is on the bottom with no washer under it, the SCC cable terminal is essentially mounted in a way that is closest to the battery… so I’d say it’s acceptable as well. Maybe it’s because I’m on my I can’t see it, but if a) the nut is not a flanged nut at a minimum and b) there is enough thread depth to permit a washer I’d ideally want a washer between the nut and the terminal. The primary purpose of a screw or stud is to provide compression pressure on two interfacing conductive surfaces. At a microscopic level the two interfaces of flat conductive surfaces are an irregular, rough interface.

The greater the compression, the more the irregular surfaces intertwin providing for better conductivity of the interface.

The percentage of total interface current flowing through the screw or stud is a small percentage of total interface current.

The greater the area, with sufficient compression, the lower the interface resistance. The larger the screw or stud size the greater the compression force that can be achieved. There is a practical relationship between surface interface area and pressure, i.e. sometimes more pressure on a smaller contact area yields similar net interface resistance to a larger contact area, depending on contact surface roughness and oxidized/contaminated interface surfaces. Aluminum surface grows aluminum oxide very quickly which is non-conductive.

Using a lug with a significantly larger hole than compression screw or stud reduces the primary conductive interface surface area.

Using a wide lug with a small screw or stud may not provide uniform compression across the width of lug surface interfaces. Using a strong (thick) flat washer, on top, helps distribute the compression force evenly across the interfacing surfaces. A small headed screw or nut can 'pucker' the lug in the center reducing the contact interface pressure toward the outer edges of lug, effectively reducing the electrical interface and increasing contact resistance.

A typical 2x20x70 mm bus bar to aluminum LFP cell terminal 'good clean' compression interface has about 0.05 milliohms of resistance. The nickel-plated bus bar has about 0.07 milliohms of resistance by itself. At the bottom of the attached drawing note the amount of heating of the terminal/bus bar for various levels of current.

Thanks for all the detailed replies, but I may have caused a confusion..

The single "m10-on-m8" occurrence is only the lug (m10) on the cable coming *from* the battery on the m8 busbar stud (this is the lower lug in the picture). The upper lug (also m10) is the cable coming *from* the inverter. I guess in total this is actually a "m10 (lug)-on-m10(lug)-on-m8(busbar stud)" configuration. SCC cables are not pictured.

The connections on the actual batteries and inverter themselves will be correct (m8 lug on m8 battery terminal, m10 lug on m10 inverter terminal). Furthermore, my batteries are 2 x LifePo4 batteries in parallel. I have no access to the series strings inside each battery.

The feedback I was looking for was if my m10 (lug)-on-m10(lug)-on-m8(busbar stud) looks sufficiently good (namely, the angles of the 2 m10s to each other is of question).

Well the nut threads are fully engaged so that’s a non-issue. And as long as the battery ring terminal is on the bottom with no washer under it, the SCC cable terminal is essentially mounted in a way that is closest to the battery… so I’d say it’s acceptable as well. Maybe it’s because I’m on my I can’t see it, but if a) the nut is not a flanged nut at a minimum and b) there is enough thread depth to permit a washer I’d ideally want a washer between the nut and the terminal.
No flanged nuts are being used. I'm using the standard design that victron recommends in their docs: nut->washer->nut->lug (or in my case, 2xm10 lugs). You can see this here: https://www.victronenergy.com/upload/documents/Datasheet-Busbar-250-A-4P-and-6P-with-cover-EN.pdf

I'm not sure of the logic of this design, I just followed the docs.

Thanks

JT
The connections on the actual batteries and inverter themselves will be correct (m8 lug on m8 battery terminal, m10 lug on m10 inverter terminal). Furthermore, my batteries are 2 x LifePo4 batteries in parallel
fine
This is what I have
namely, the angles of the 2 m10s to each other is of question
Other than my ocd not liking the 92.3* angle instead of a machinist’s true 90* ? LOL that’s fine.
No flanged nuts are being used. I'm using the standard design that victron recommends in their docs: nut->washer->nut->lug (or in my case, 2xm10 lugs)
Fine. Electrical flanged nuts have circumferential ridges that sortof act like a locking facility for the nut, but proper torque of the lower nut then ‘jammed’ by the top nut over a washer is just as effective or more so. I like a flanged / washer head nut at a minimum but prefer a washer between the terminal and the nut to not present rotational force on the terminal as well as present the clamping force over more surface area while not deforming the terminal in any fashion.

We just all hyper-OCD’d the thing but maybe someone learned important safety information.

Choosing the Right Cable Lugs for Your Electrical Projects

Choosing the Right Cable Lugs for Your Electrical Projects
Cable lugs are vital components in any electrical system, serving as the connectors between wires and terminals. These small but essential pieces ensure that your electrical connections are secure and reliable. In this article, we will explore what cable lugs are, their importance in various applications, and how to select the right ones for your projects.
 

Understanding Cable Lugs and Their Importance


Cable lugs are designed to connect cables to electrical terminals, providing a solid mechanical and electrical connection. This makes them crucial for the safety and efficiency of electrical installations. Without properly selected and installed cable lugs, systems can suffer from poor connectivity, leading to overheating, malfunction, or even catastrophic failures.

The applications for cable lugs are incredibly diverse. In industrial environments, they are often used to connect large gauge wires in machinery and equipment. In renewable energy projects, such as solar power systems, cable lugs facilitate connections between solar panels, inverters, and batteries. Residential wiring also relies on cable lugs for secure connections to circuit breakers and other components. Understanding these applications will help you better serve your customers and meet their specific needs.
 

Key Considerations When Selecting Cable Lugs

Material Selection: Copper vs. Aluminum


One of the first things to consider when choosing cable lugs is the material. The two most common materials are copper and aluminum, each with distinct advantages and drawbacks.

Copper lugs are renowned for their excellent electrical conductivity. They provide a low-resistance connection, which is critical in high-performance applications. Additionally, copper is highly durable and resistant to corrosion, making it ideal for harsh environments. However, this quality comes at a cost, as copper lugs are generally more expensive than their aluminum counterparts.

Aluminum lugs, on the other hand, are lightweight and more cost-effective, making them an attractive option for budget-conscious projects. Though aluminum has lower conductivity than copper, advancements in alloy technology have improved the performance of aluminum lugs significantly. These lugs are suitable for many applications, particularly where weight savings are essential. Weighing the pros and cons of each material will help you make informed decisions that align with your customers' requirements.
 

Getting the Right Size


Another crucial factor in selecting cable lugs is size. Each lug must match the diameter of the cable to ensure a proper fit. If the lug is too small, it may not make adequate contact, leading to high resistance and potential overheating. Conversely, if it’s too large, it may not grip the cable securely, resulting in a loose connection.

To avoid these issues, always refer to the manufacturer’s specifications. Educating your customers on how to measure cable diameters and match them with the appropriate lug size will enhance safety and performance in their projects. A well-fitted cable lug will provide a reliable connection that withstands the demands of the electrical system.
 

Connection Types


Cable lugs come in various connection types, including crimp, screw, and bolt. Each type serves different purposes, and understanding these distinctions can significantly impact the reliability of the connection.

Crimp lugs are widely used in industrial applications, where a permanent connection is essential. They are attached using a crimping tool, creating a strong bond between the cable and the lug. Crimping ensures a secure connection that can handle the electrical load without failure.

Screw lugs are versatile and easy to install, making them suitable for a range of applications. They allow for quick connections and disconnections, providing flexibility in installations. This is particularly useful in situations where equipment may need to be serviced or replaced.

Bolt lugs are typically used for larger cables and high-current applications. They require a bolt for attachment, ensuring a secure connection that can handle significant electrical loads. This type of connection is often found in power distribution systems, where reliability is paramount.

By providing your customers with a clear understanding of these connection types, you can help them select the right lugs for their specific applications, enhancing the overall performance of their electrical systems.
 

Voltage and Current Ratings


Every cable lug has defined voltage and current ratings, which are essential for ensuring safety and efficiency. Selecting lugs that meet or exceed the necessary ratings is critical to prevent overheating and potential failure.

When sourcing cable lugs, it’s vital to check the specifications carefully. Educate your customers on the importance of adhering to these ratings. For instance, using a lug rated for lower voltage or current than required can lead to serious safety hazards. By emphasizing these points, you can help your customers make safer choices and avoid costly mistakes.
 

Compliance and Standards for Quality Assurance


In the electrical supply business, familiarity with industry standards is crucial. Standards such as those set by the International Electrotechnical Commission (IEC) and the American National Standards Institute (ANSI) provide guidelines for the safety and performance of electrical components, including cable lugs.

Compliance with these standards ensures that the products you offer are safe and reliable. This builds trust with your customers, who can be confident that the lugs they purchase meet recognized safety benchmarks. When partnering with suppliers, make sure they provide documentation to verify compliance with these standards.

Opting for certified products is another way to ensure quality. Certification indicates that the lugs have undergone rigorous testing to meet specific safety and performance criteria. This added assurance can enhance your product offerings and differentiate you from competitors who may not prioritize quality.
 

Finding the Right Suppliers


Choosing the right suppliers is essential for maintaining quality in your inventory. Look for suppliers with a solid reputation in the industry. Reliability, quality, and customer service should be your top priorities when selecting a partner for cable lugs.

A good supplier will not only offer high-quality products but also provide excellent customer support. This includes timely deliveries, responsive communication, and assistance with any issues that may arise. Building strong relationships with reliable suppliers can lead to better pricing, exclusive offerings, and improved service for your customers.

Balancing cost and quality is key. While it might be tempting to opt for the lowest price, investing in high-quality cable lugs can save you money in the long run. High-quality products are less likely to fail, which reduces the risk of returns and enhances customer satisfaction.
 

Installation Tips for Better Performance


Proper installation of cable lugs is vital for optimal performance. Educating your customers on best practices can help them avoid common pitfalls that lead to failures. Encourage them to follow the manufacturer's guidelines during installation to ensure a secure fit.

One of the key aspects of installation is using the right tools. Crimping tools, torque wrenches, and other equipment are essential for achieving a reliable connection. Providing your customers with a list of necessary tools can enhance their experience and satisfaction.

Additionally, consider offering installation training or resources. This could include video tutorials, instructional guides, or workshops. By empowering your customers with knowledge, you help them achieve better results in their projects.
 

Common Mistakes and How to Avoid Them


There are several common mistakes that can occur when selecting and installing cable lugs. One significant issue is compatibility. Mismatching lugs with cables or applications can lead to serious problems down the line. It’s important to ensure that the lugs chosen are suitable for the specific cables being used.

Environmental factors also play a role in the performance of cable lugs. Temperature, humidity, and exposure to chemicals can affect the longevity and reliability of connections. Educating your customers about these factors can help them make informed choices that enhance the lifespan of their electrical systems.

Regular maintenance and inspections are essential for ensuring the longevity of cable lugs. Encourage your customers to check their connections periodically. Simple inspections can reveal issues like corrosion or loose connections, allowing for timely repairs that prevent failures.
 

Open-Minded Considerations


The electrical component landscape is continually evolving. Staying informed about new materials, technologies, and trends can give you a competitive edge. Attend industry conferences, subscribe to relevant publications, and engage with other professionals to keep your knowledge current.

Additionally, engaging with your customers can provide valuable insights into their needs and challenges. Regular feedback can help you understand what products and services are in demand, allowing you to adapt your offerings accordingly. Being open-minded and responsive to customer needs can enhance your reputation and drive business growth. Message If you have any suggestions or question for us.Please contact us. * * * *

If you are looking for more details, kindly visit Electric Powertek.

For more cable lug manufacturerinformation, please contact us. We will provide professional answers.

Please visit our website for more information on this topic.

2

0

Comments

Please Join Us to post.

0/2000

All Comments ( 0 )

Guest Posts

If you are interested in sending in a Guest Blogger Submission,welcome to write for us!

Your Name: (required)

Your Email: (required)

Subject:

Your Message: (required)